wingnut771
Honorary Master
What are we looking at?
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
What are we looking at?
No eskom power used on geyser since 9 Jan, running only on solar PV.What are we looking at?
Why does it use all different watts?No eskom power used on geyser since 9 Jan, running only on solar PV.
Even at 55.2V?
Can you set absorption time on inverter? I would take SOC counter readings with bag of salt.Yes. Only under certain conditions. Let's say the battery is at 96% as per bms SOC and I draw something heavy and it drains and then switches back to charging at 100% it gets that OVP warning.
If there is no load on the battery and it charges normally then at that voltage it seems to cut out at around 89% SOC and just stays there. It doesn't go higher.
At 55.6 which it is now it does go to 100% eventually
Don't have that on the luxpower can only set the float and absorption voltageCan you set absorption time on inverter? I would take SOC counter readings with bag of salt.
Can you set absorption time on inverter? I would take SOC counter readings with bag of salt.
It probably resets to 100% when cell 5 hits OVP.I don't think so but I will have a look.
It probably resets to 100% when cell 5 hits OVP.
Are you using lead acid mode?I don't know![]()
As far as i have it some solar geyser setups uses 3 panels with an mppt basicly running element directly from the panels ie no inverting to 220v acWhy does it use all different watts?
Having a charge voltage that is lower the amps will drop off and take longer to get full as long as it still accept charge 1A or more the bms will keep balancingYes. Only under certain conditions. Let's say the battery is at 96% as per bms SOC and I draw something heavy and it drains and then switches back to charging at 100% it gets that OVP warning.
If there is no load on the battery and it charges normally then at that voltage it seems to cut out at around 89% SOC and just stays there. It doesn't go higher.
At 55.6 which it is now it does go to 100% eventually
Looks like his charge voltage is 57.6V.Having a charge voltage that is lower the amps will drop off and take longer to get full as long as it still accept charge 1A or more the bms will keep balancing
On many they only balalance while charging and only when cell voltage pops over 3.45v
Tha battery spends verry little time there normally
They don’t push from the panel straight to the element otherwise it won’t meet certification for the thermostat.As far as i have it some solar geyser setups uses 3 panels with an mppt basicly running element directly from the panels ie no inverting to 220v ac
The wattage then depends on solar output as clouds roll over or angle changes wattage changes
I haven’t fed AC to geyser since November. 4x340W panels.No eskom power used on geyser since 9 Jan, running only on solar PV.
I'm using a Geyserwatcher connected to 3 x 550w panels.
Its on 55.6V. It was in AGM mode but I changed it last night to User Defined. Lets see if that makes any difference.Looks like his charge voltage is 57.6V.
Set bulk/absorb to 56V and float to 53.6V.Its on 55.6V. It was in AGM mode but I changed it last night to User Defined. Lets see if that makes any difference.
Float? I thought lithium doesn’t floatSet bulk/absorb to 56V and float to 53.6V.