soulie
Expert Member
1 metre preferredThanks for the info i thought it could carry more
Horizontal fixed to wall with clips 2m run?
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
1 metre preferredThanks for the info i thought it could carry more
Horizontal fixed to wall with clips 2m run?
have you measured it ?what temp will the cable run at ?does the sun heat it?Even with a correction factor of 0.6, I still get 9KW.
OP's talking about a garden shed close to his flat, distance is going to be 10-20 meters at most, we're not talking a long distance.
Have you? I don't need to get into a pissing match with you here.have you measured it ?what temp will the cable run at ?does the sun heat it?
the max you can go on a 10mm cable is table 8 which is around 64 amps with no correction factor ,if you multiply a 0.6 factor you will get around 8.5 kw max .i would still rather work on table 5 at 55 amps it also depends on what cable is usedHave you? I don't need to get into a pissing match with you here.
Was refering to the 24v AM2, that was a quick interner search, and yes prices are crazy at the moment.Hubble AM2 for R20k?
Can't you put up awnings above windows and doors?That I know is unfortunately not allowed in the complex.
you can rather go big than regret it .you may not use 55amp (yet)but i can see that 8kw unit peeking out of the corner .The idea on the cable will be to have it buried, entry will be at floor level into the kitchen, and from there routed internally to the panel, will be in trunking. So exposure to sunlight will be minimal, I wil also have the exposed exterior runs in bosal, even though it is armoured. Yes overkill, but the slight extra cost/effort is worth it.
As some mentioned, a 10mm cable might be overkill, but if you take that 5kw inverters can spike to 10kw for short bursts I would rather have a bigger cable.
And yes, this forum is for advice only, I always confirm everything with my electrician. Who will trust a group of strangers on the internet.
Maybe if you go Victron, but the Sunsynks won't, they'll just trip.The idea on the cable will be to have it buried, entry will be at floor level into the kitchen, and from there routed internally to the panel, will be in trunking. So exposure to sunlight will be minimal, I wil also have the exposed exterior runs in bosal, even though it is armoured. Yes overkill, but the slight extra cost/effort is worth it.
As some mentioned, a 10mm cable might be overkill, but if you take that 5kw inverters can spike to 10kw for short bursts I would rather have a bigger cable.
And yes, this forum is for advice only, I always confirm everything with my electrician. Who will trust a group of strangers on the internet.
I am thinking of building a portable frame I wheel out in the mornings and store in Garage in afternoons. Yard not big enough for another temp structure. Winter I might still have a problemSo I like the idea of the ground mounted panels as suggested by @TheChamp . All that you have to do to fool the trustees is to make it look like a shed. So design a structure that 1) points your panels where you want them and 2) has walls covered with IBR (and even a fake door). They won't know the difference.
You are very lucky to have a garden unit, think of all the poor fsckrs without![]()
Just make sure that the panel frames are earthed.I am thinking of building a portable frame I wheel out in the mornings and store in Garage in afternoons. Yard not big enough for another temp structure. Winter I might still have a problem
They will be made from pine. That's earthy enough.Just make sure that the panel frames are earthed.
What happens if they’re not?Just make sure that the panel frames are earthed.
I guess if Zeus gets angry you can fry all your equipment.What happens if they’re not?
Zeus should strike the earthed stuff first afaik.I guess if Zeus gets angry you can fry all your equipment.
Only if you sacrifice a hippy.Zeus should strike the earthed stuff first afaik.
It depends. Touching the frames can give you anything from a buzzy trickle shock to a full-blown man down.What happens if they’re not?
All the more reason to earth them. Wooden frames are notorious for nice big shocks.They will be made from pine. That's earthy enough.![]()
your frames must all be bonded to earth as the potential must be the same throughout the system .but not to your homes earthWhat happens if they’re not?