You misunderstand me. What I meant was that in the geyser circuit, there must be a CB. The circuit breaker's job is to protect in over-current situations. If your geyser is similar to mine, you will probably have a 20A type B CB and 2.5mm^2 wire feeding the geyser (for 3kW). The type B CB will break at a current of around 60-100A (3-5 times the rated current). Although it will get hot, the 2.5mm^2 wire will probably survive a short time experiencing high current.
Now you introduce your POW R2 into this circuit. It is rated for 16A. What happens if, for some unknown reason, your element experiences a short-circuit? What happens with the Sonoff if 100A flows through before the CB breaks? Does it short or open? Does your home automation device now essentially become a fuse?
That is what I meant when I stated that it is the job of the CB to protect the circuit. I wasn't expecting the Sonoff to act as protection.