Or can I plug the power of the ups out, but it's still connected to the battery terminals. The external charger will be permanently connected and switched on. Can this work perhaps.
All the plugging this in and plugging that out and switching this on and that off.....is not the way to go. You are going to make up Fup somewhere sooner or later. Do have loadshedding tonight?
How many AH bateries each ?
How strong charger in amps ?
All the plugging this in and plugging that out and switching this on and that off.....is not the way to go. You are going to make up Fup somewhere sooner or later. Do have loadshedding tonight?
How many amps can external charger provide ?
All the plugging this in and plugging that out and switching this on and that off.....is not the way to go. You are going to make up Fup somewhere sooner or later. Do have loadshedding tonight?
12amps
Load percentage on ups when running ?
I don't understand your question
Load percentage on ups when running ?
How much load (shown as a % on most UPS software interfaces) is being placed on the UPS?
Do you have software loaded ?
That pic saying 4%
I am trying to figure out how deep you will discharge battery in 2 hours
This will give me an indication how fast you can get battery recharged.
hope he is not hinting towords running ups as if it an online ups![]()
If internal charger of ups is current limited to max 2amps
And external charger can give extra 12 amps
So thats a max of 14 amps
If bateries 50% empty
Will take about 4 hours to charge back to near 100%
Will not hurt ups as it thinks external charger an battery