Hi,With the Sunsynk you will need to balance the two MPPTs as per Keith Gough (Sunsynk CEO and chief techie). To achieve an optimal arrangement with only six panels is going to be very difficult, if not impossible. You ideally want a higher voltage on your strings to kickstart the MPPTs as early as possible in the mornings, and stop as late as possible in the evenings, so closest to 400V as possible. The Sunsynk's MPPT range is 125-425V, so it will only start producing power when the panels are giving at least 125V. You did not give the exact specs of the CS panels that you selected, so its difficult to say, but looking at some other CS panels, they appear to produce around 48.8V open circuit, but only 40.9V under full load (load drops the voltage). 3 in series on each MPPT will therefore initially produce 146.7V, but as soon as the inverter "combs" the load across to draw from solar, the voltage will drop to 122.7V, and cause the solar load to be "combed" back. So the MPPT will probably flap up and down, and the inverter too.
Obviously this needs to be verified with the exact model of panel that you have (mind posting it?), but not a situation that I would want to endorse. Did the person who sold you this explain it to you? You may want to consider returning the panels in favour of some panels that they do have sufficient stock of, to at least allow for a working system while you wait for the balance. I know that panels are difficult to get right now, and there is some price-gouging, but I would rather source equipment from a reputable source that knows and understand what they are selling, what the limitations are, and who can advise you on such caveats.
Thanks for the input.
I am definitely getting the last 4 panels to make 10 in the next week or 2. So my plan was to have 5 x 49.3Voc = 246Voc per string.
Would you still suggest one string per mppt?
Would there be any benefit to putting the strings in parallel to up the amps to 22?
Thank you