The 5K does have one fan. The 8K has 3.What about the 5kW? I think that has no fans.
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
The 5K does have one fan. The 8K has 3.What about the 5kW? I think that has no fans.
Excellent results, you have summarized it pretty well.
On the panels, placing East/West and North on the same MPPT will not have the greatest outcome. You may want to consider a baby (2- 3.6K max) Solis on the Aux to provide another 2 MPPTs. It's cheap, and you can have East and West on the Sunsynk, and one of the Solis MPPTs facing North. And another MPPT spare to play around with![]()
I have considered this with my 5K Sunsynk, and would probably have done it already if I weren't seriously considering relocation.
I don't think each string is independant. IIRC the strings are bonded together at the inverter.Why? It was your explanation of each string being independent that finally made it make sense to me and not each MPPT.
I don't think each string is independant. IIRC the strings are bonded together at the inverter.
You could perhaps go east/west of you put optimisers on the strings. You'll lose quite significant production otherwise as strings revert to the lowest performing panel.Good point, these are the confusions of my life.
I wonder if having East and West on one MPPT wouldn’t be a weird hack considering only one would be “online” at a time.
But even so how much of an efficiency loss are we really talking about here? Is it a 1% or a 5% or a 50% equation @RonSwanson?
And for absolute clarity while we discuss it, the voltage limits are per string, not per MPPT right ?
2P strings on east/west (one string east, one string west) on one MPPT1, one string north on MPPT2.You could perhaps go east/west of you put optimisers on the strings. You'll lose quite significant production otherwise as strings revert to the lowest performing panel.
2P strings on east/west (one string east, one string west) on one MPPT1, one string north on MPPT2.
2 strings in parallel.
Mine is also in the garage. When my workers open the door to the garage that's just down the hall from my home office door i can hear that sweet sound of those 3 fans cooling down my free energy machine quite loud. I would not mount inside the house if at all possible.@SauRoNZA keen to get another opinion on the fan noise of the 8KW Sunsynk, how are you finding it? I may have the 8KW Deye installed in my entranceway close to the lounge, in a (ventilated) cupboard/enclosure, but a bit worried about fan noise.
When it comes to shading of one panel in a string, yes, it will affect that string only. If you orient one string azimuth East, and another West, and then use the same MPPT, the lower voltage on either string (before and after 12H00) will pull the overall MPPT down. It's most efficient to dedicate an MPPT for panels with the same azimuth and tilt.Why? It was your explanation of each string being independent that finally made it make sense to me and not each MPPT.
Per MPPT.Good point, these are the confusions of my life.
I wonder if having East and West on one MPPT wouldn’t be a weird hack considering only one would be “online” at a time.
But even so how much of an efficiency loss are we really talking about here? Is it a 1% or a 5% or a 50% equation @RonSwanson?
And for absolute clarity while we discuss it, the voltage limits are per string, not per MPPT right ?
Does the voltage not stay constant?When it comes to shading of one panel in a string, yes, it will affect that string only. If you orient one string azimuth East, and another West, and then use the same MPPT, the lower voltage on either string (before and after 12H00) will pull the overall MPPT down. It's most efficient to dedicate an MPPT for panels with the same azimuth and tilt.
Per MPPT.
2 strings in parallel.
When it comes to shading of one panel in a string, yes, it will affect that string only. If you orient one string azimuth East, and another West, and then use the same MPPT, the lower voltage on either string (before and after 12H00) will pull the overall MPPT down. It's most efficient to dedicate an MPPT for panels with the same azimuth and tilt.
How does that change things? Runs them both as one but would effectively only be one at a time due to East and West being so far removed?
We run roughly East and roughly West PV strings with 5 Canadian Solar 360w panels in each string through a Victron 250/70 MPPT. Early morning and late afternoon there is only one string active but the closer we are to midday the more both strings are active, I have seen PV power peak at more than the combined kW rating of each string in the middle of summer. This setup does suffer in winter though, the angle of the sun plays a huge part and we have issues with shading early morning and late afternoon.
Yeah for me the East and West would be purely supplementary to the North strings.
So the question would really be if the efficiency loss is worth the complexity and cost of an external MPPT.
And if I do go that route I might as well leave everything north facing “as is” and then just buy 10 more panels and put 5 on the East and 5 on the West.
I also have the 8kw Sunsynk, the fans are too noisy for installation inside a house unless it is enclosed (you will need decent cooling plus it will have to be designed to keep the dust on the outside of the enclosure as these tend to suck dust inside)@SauRoNZA keen to get another opinion on the fan noise of the 8KW Sunsynk, how are you finding it? I may have the 8KW Deye installed in my entranceway close to the lounge, in a (ventilated) cupboard/enclosure, but a bit worried about fan noise.