Problem is - everything is unplugged on the circuit when it trips, all the switches are also off... So no clue. Probably going to have to get an electrician. Good way to spend my Saturday.
Say it's Circuit 6, by itself, I can use it - with eveything plugged in.
If I turn on any of the other circuits it trips EL, even if nothing is plugged in and all the switches are off on Circuit 6.
If I leave circuit 6 off, all the other circuits work.
So the important thing to understand is this, there is some level of leakage between your live and earth or even neutral and earth or live and neutral.
In this case, probably from live, because it only happens when turning on things.
Now if you short them live and neutral, thats 100% leakage right?
The EL, would have a certain level at which it trips. Lets say, 0.01% leakage between live and something.
Every device in a house, has some form of leakage. It is just how it is. It sounds like, you have something with higher than normal leakage on circuit 6. Could be a device, could be that wire or plug points on it etc.
So, if you only have circuit 6 on, its below the EL trigger level.
or If you turn off circuit 6 and everything else on, its below the EL trigger level.
Basically, you need to find that thing, on circuit 6, which has too much leakage. Could be open wires where water flow through, or even not water but just high humidity. Could be a device/appliance on that circuit.
Its a mission to find. Best of luck is all I can say. These things are annoying. I had a sort of similar issue, which had me cut out a complete wire, buying a new one at R2500 (100m surfix) and run a new line myself to get rid of my EL trips whenever it rains. That was my nuclear approach to solving my own issue, but I at least sort of figured out why mine happened.