Make sure inverter is power on from the mains.
Make sure that the battery is off.
Open the battery isolator
Use the point of the isolator towards the inverter to plug the external battery.
Inverter wakes up, initializes and when it's done it start charging my battery, (the Jumpstarting battery)
Take the jump-start battery off, inverter still on, close the battery isolator.
Power the battery on, few seconds after the battery shows signs of life with SOC LEDs it trips the whole thing down.
I repeated the process a couple of times hoping with no luck.
Could possibly be that the BMS in the batteries have not woken up to change its state to allow charge/discharge, Had a customer experience similar setup (4Xus3000 and Kodak king) battery completely refused to charge or discharge. After it was discharged too low. Below is what I sent to them that helped ( Little Edit here and there )
When you switching the battery isolator to on for the Pylons, the state of the BMS is on protection so when the inverter is happily trying to charge it, BMS is no no I take you down.
You can disconnect the batteries from the inverter and from each other if you have more than 1 batteries connected up.
Switch the battery on and hold the SW button for a few seconds till the soc led start flashing and leave them till they stabilize, once they are solid this would of woken up the BMS and then you can
test the voltage on the battery terminals, if it shows a voltage then the BMS has woken.
Do this for all the batteries, and then when you have got a voltage from all the batteries. Connect them back up together but still not connected to the inverter, Start up all the batteries and just press the SW on the master again for
a few seconds, all of the soc leds on all the batteries should flash to establish a connection between them, give them a few minutes to stop flashing and then test there is a voltage coming out from the leads that will be connected to the inverter.
Shut Down, Hook up batteries to the inverter. With the inverter still switched off and AC off, Start up the batteries, SW button on master, slaves flashy and bow solid. Give it a few seconds then switch the inverter on, Give it a few seconds to let the
inverter know there is batteries and for the Pylons to know its being discharged, if there is no trip, Switch AC on
(Check voltage on the panel and if its near cut of voltage, drop the cut off voltage to 44V) so this will give you some time to switch the AC on and charge the batteries and then have the settings back to the recommended.
You mentioned no communication. What settings are you running also on Program 5/12/13/26/27