Are you sure the CT wires werent switched around when installing new inverter?Hi guys,
I just had my inverter changed from a 5kw to a 8kw deye but there seems to be a funny situation with the CT. CT is exactly the same as it has been on the db and eskom side but it looks almost like the inverter is confusing the two CT readings ie: internal and external.
Example:
View attachment 1708197
so if there is no non-essential draw there is always the differance of 20w or so which is what the inverter normally allows to draw from eskom to test connection.
So before, it was plain to see, External CT was grid at say 500 and internal CT was at 480 with the differance being the draw by the non-essentials. Now as above, it seems to e swopped? The internal CT is higher than the external which means and showing negatives on my essentials at times because of the differance. Also I noticed a while back that the cummulative grid usage would not increment. with non-essential use, giving me a false daily total basically sans the non-essential draw from grid.
Now with the CT in the same spot and direction, I can only assume its something with the connection on the board of the inverter or am I totally wrong here?
Solarman dongle and inverter both read the same for those readings so there doesn't seem to be a discrepancy between the inverter and dongle.
EDIT: Not the coil itself... but the 2 wires that plug into the inverter.