Hi all,
I have been watching this thread for a long time, reading and learning, cross checking info, and i would like to thank all those that freely shared knowledge from the bottom of my heart.
As a result, I bought an Axpert 5K, a few solar panels, batteries, and a 5.5 KVA Generator, and want to finally install them permanently into the house wiring. Step one will be inverter, batteries and generator to survive the severe 5 day outages we experience where i live. Step two will be to put the panels up, but that will have to wait a bit.
The wiring of panels and batteries i will leave out of the scope of this discussion for the moment.
What this post deals with is the safe wiring of inverter and standby generator permanently into the mains supply, specifically the correct E/L behaviour via neutral earth bonding.
My design, after a hell of a lot of reading, i have posted here:
http://s7.postimg.org/9jgr6kfl7/House_Wiring.jpg
I will update this post and that image as needed to have all details and reasoning described and questions answered, and hopefully it will be useful to someone else. I also have aspirations to get my "going off grid" experience onto a website, but that too will have to wait.
I will be completely replacing the existing DB board, and getting a knowledgeable electrician in to do the COC afterwards.
I do not know such an electrician, so a referral would be great, as i will get him to approve the design before i even start the work.
Let me attempt to talk through the diagram:
I get three phase power to the house delivered to an outside supply box.
These are indicated top left, along with my house's earth spike.
The three live wires go through a breaker, while the neutral does not.
Those cables then run to a box inside the house i have named the Mains/Genset Changeover box.
The three phases run through a prepaid meter, and note that the generator does not or one pays for petrol AND the consumed power. While paying for both is OK in a short term emergency, the idea really upsets me.
Note: I need a mechanism to safely and manually, select between any of the three phases, or the generator if all three phases are not working properly. We have blackouts, brown outs and over voltages all the time, and i have responded in a later post why i need to switch between phases from time to time. I understand the need to balance phases, and there are other houses on our plot that we include in the balancing excercise.
I cannot find 4-input changeover switches in the required current rating, and so have cascaded three regular switches.
I chose the knob type selector switches over the DB board rail mount switches, as those examples of the latter i managed to find are really tough to switch and the wife and kids need to be able to do it easily. I will add lights and voltmeters to the panel so one can easily see the state of the various phases and generator power.
An important note here is that the switches need to be "break-before-make" type, so that you never short phases to each other or the generator.
The first switch is a single throw switch, allowing selection between the first two phases.
Output of that switch runs to a second identical switch along with the third phase.
I now can choose a mains phase between them, and no switch position is ever going to be a problem when phases come on or off.
The output of the second switch is now my mains, much like a house that runs from a single phase, of which i have a Live and Neutral.
These wires are run to a third switch which is a double throw switch. The second input to this switch is the Live and Neutral from the generator itself. This allows safe selection between mains and generator. This switch is wired so that one set of contacts switch between Mains and Generator LIVE, and the second set between Mains and Generator NEUTRAL. This ensures complete separation of upstream wiring.
Side note: The Axpert has a relay that can start a generator when mains power fails or batteries are low. If ever i implement that, this is the switch that will be replaced with the automatic switch. Also, the generator can be started at any time without it being a problem.
FIRST NEUTRAL/GROUND BOND: The generator neutral is bonded to earth BEFORE this switch, so that the bond is isolated when connected to mains, and active when the generator is selected.
Output of this switch, Live and Neutral then is run to the house DB board main switch, along with Earth and Neutral.
I am planning to have a two row DB board, where the first row is used for appliances powered by mains, and the second row dedicated to those that will run off the inverter. Currently, there are three separate neutral bus bars, and this was done to incorporate what i learned on this thread. It is open to criticism; this is why i posted.
First row has the mains breaker, which breaks both live and neutral.
Neutral goes to its own busbar.
Live goes to the first breaker that feeds the Axpert Mains IN, feeding the inverter "clean power".
Live also goes to Mains Row E/L, which in turn has its own neutral bus bar, not connected to the first.
After the E\L, live is fed to a couple of breakers that run those appliances that i cannot afford to run off batteries, and i can add more as needed. These appliances are E\L protected.
The Axpert Mains OUT is then fed to its own E/L in the second row of the DB.
This E\L outputs to a third, dedicated neutral bus bar.
SECOND NEUTRAL/GROUND BOND: Note that the Inverter Output Neutral is bonded to earth BEFORE the E/L.
From what i have read, this bond SHOULD NOT exist when the inverter is relaying mains on bypass mode.
From reading it seems the manufacturer has a relay in the case that bonds neutral to earth when supplying from the inverter, and breaks the bond when in bypass mode. I am nervous to make this assumption, and i need to figure out a way to test this. If this feature doesn’t exist, an automatic contactor is required to make or break this bond based on whether there is power on the top row Mains Switch.
After that, it is straight forward, the second E/L feeds a row of breakers.
Your thoughts, ladies and gentlemen, are welcome, and much appreciated.