Axpert MKS 5kVA inverter installation
Hi,
I installed one of these Axpert MKS 5kVA inverters over 4 days (two weekends). Here's my story.
(
Disclaimer: I have an EE background; working on mains electricity can be lethal - get professional advice first. See my list of essential and life-saving equipment at the bottom of my next post)
My main aim was to just survive load-shedding with an option to add PV solar panels at a later date, should I choose to. The 3kVA and 5kVA units just appeared on the Rectron price list, so I ordered a 5kVA. The 3kVA unit runs on 24V and has a max PV capacity of 600W. The 5kVA runs on 48V and has a max PV capacity of 3000W - the 5kVA was a no-brainer choice.
I decided that I wanted the inverter fully integrated into my house wiring, carrying only "low current" devices. All the "high current" stuff, like geyser, oven, aircon and washers (wetter and dryer) would be driven only from the municipal feed. That effectively left the rest of my house to be carried by the 5kVA inverter (note: I have gas stove for cooking).
The first task was to split my DB into high-current and low-current sections. I was lucky that it was almost 80% ready for that - just had to cut my Live busbar and pull through a few wires towards my washer appliances.
Here are the two sections along with the earth busbar:
I used 6mm² fixed-wire cable from Aberdare, rated at 43A (SANS tested and rated), to wire the DBs together as well as for the internal wiring. This is ample to/from the Inverter, which is itself rated at 27A on the 240V side.
Next, I had to add a second DB to house all the safety and change-over switches in order to by-pass the inverter for any reason. My Generator by-pass switch is also housed in this same DB:
From left-to-right, the switches are: Inverter isolator, inverter-bypass, generator-change-over, inverter output trip switch. Can you spot a problem? Yes, the isolator on the left should be a beaker (more on this later).
The connection on the inverter itself is pretty straight forward. Bend the cables so minimize stresses and make sure all the strands are bunched in two layers to fit into the screw terminal blocks of the inverter. Any screw terminal connection must be mechanically strong and sound. You don't want bad contacts spoiling your day.
Next, make sure everything is accurately labelled:
At this point, the inverter will not fire up yet - it needs to have a floating DC supply before it will switch on. However, this is where I stopped and took a breather. I could flip down the inverter by-pass switch to test what I already had so far and make sure that part worked as expected.
I plugged in my 3-pin outlet tester and verified that my existing and new wiring was working and everything was wired correctly. The 30mA earth-leakage was also tested to be working. This is an essential testing tool; I bought mine from Communica at a sale for R35.
Next was installing the batteries and associated cabling. I used 25mm² flexi cable (basically the same stuff used for welding). The Aberdare spec says this stuff is rated at 104A DC:
I tested the cable over a 3m length with a 30A load. It dropped about 150mV over 3m, which means (using ohm's law) it has a 5mΩ resistance per 3m length. At 100A that would mean that I would drop half a volt over the length of the cable - so the aim was to keep it as short as possible. I ended up using two 1.3m lengths (one for positive, one for negative) towards the batteries.
The connections on the ends need to be really sound - make sure you get a proper ring connector and crimping tool for the job. The Axpert manual is very clear and helpful in specifying exactly the connector types you need. The crimping tool is a different story: it's way expensive. I was fortunate to be able to borrow my company's crimp tool:
Don't skimp on this part! The DC currents drawn by this inverter is in the order of 86A - that's a lot of energy (the 3kVA is even higher at 100A). If your DC connections and cabling is not adequate you will have a guaranteed fire hazard!
Continued in next post (due to the silly 6-attachment limit... urgh) ....
--deckert