So what would you suggest for a 24v system
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
As all of them are for "automotive" applications, and only one provides a voltage rating of 32V, I think it's safe to assume that all these fuses are rated only at 32V. They are thus no good for 48V battery banks.
Automotive (car) fuses are also fast blow fuses, not ideal. You ideally want slow blow, ceramic (not glass) fuses too in any case.
A 1000V/125A Fuse holder (din mount, 22x50 cylindrical) will set you back +- R125, depending on brand
A 1000V/32A Fuse holder (din mount, 22x10 cylindrical) will set you back +- R50, depending on brand
Hi all, I am desperately looking for some assistance from one of the knowledgeable members. I bought an Axpert 3KW 24 volt MKS PLUS unit and connected four 6 volt trojan T125 cells (240Ah) with it. However I keep getting the error message stating battery overcharging. It works with no problem on DC. I got the batteries checked twice and they are okay. My electric contractor says I should have gone with 100Ah cells. However I am aware of someone using the same batteries with the same model with no problem! Can the cabling affect this? Apparently he has used 4G cable instead of 8 AMG. I am having sleepless nights having invested quite a fortune on the set up and sitting in darkness. Your help is highly appreciated!
Made by Voltronic, same guys who also make the InfiniSolar inverters. I've installed quite a few and had nothing but absolute pleasure out of them.
OP's price is rather low for the 5KVA unit though
I'm using the same batteries on my 5KVA - no issues...
Can you post pics of your battery bank (good quality pics), all the connections / crimps, and what error code(s) are you seeing?
Who did the installation, you or your electrical contractor?
EDIT: The 3KVA unit only allows for 2400W - it's easy for the unit to trip on a overload when other things AND the kettle is on at the same time. Your kettle alone will be close to (if not over) 2KW. Somehow, I smell yet another badly planned installation...
Hi Chris, thank you for the response. The installation was done by an electric contractor. I am not at home currently hence regret unable to provide the pictures. The batteries are connected in series. The inverter is Axpert 3KW MKS plus 24 volt. (Model SOL-I-AX --3M PLUS 24). The plan was to exclude the kettle and other high power utility items. I bought the battery bank and inverter based on input from experienced members in this industry on forums like this. Some are using 2 parallel banks of the 215Ah with the same model inverter with no problems. So I doubt if it has to do with one bank of 240Ah batteries.
Forgot to mention that the error code flashing is fault 3.
Forgot to mention that the error code flashing is fault 3.
I'd be pissed off with the installer if this is the case! He should check the data sheet of you batteries, and program the unit accordingly - with user values if necessary.
Just remember... Assumptions are the mother of all f-upsNot saying it is, or isn't so, but -anyone- can change those settings, very quickly and easily.
and possibly include the fridge and freezer.
Wife is paranoid about the stuff in the fridge/freezer due to milk and food for the babyJust explain to me why quickly? I get SO many customers too wanting this...
Just like your geyser, if you keep the doors closed and opening/closing to a minimum, your fridge/freezer will most certainly not get so warm as to spoil the food within a 2 or 3 hour period??
I'm just failing to understand the logic here...