Hi Everyone.
I just received my Axpert 5KVa and 8x Deltec BD-54-105Ah batteries a couple of weeks ago and had the electrician come through to install it.
My house has a 3 phase setup and 2 DB's, one upstairs and the main one downstairs. After a 3 full days of work we isolated all the plugs and lights we wanted to back up using the inverter and moved both the upstairs and downstairs circuits onto a single phase.
The inverter works fine and switches perfectly to battery when you trip the main breaker, however when Eskom cuts the power during load shedding its just displays error 58 and shuts off. You can manually restart the inverter and it will work but only with the main breaker in the off position.
It also shows an AC input of ~230V even when the utility power is switched off and the batteries are providing power to the DB. My guess is there is an error in the wiring and the inverter is being confused and detecting its own power source as the utility.
My house wiring is very complex and was a nightmare to isolate circuits, so let me know if you would like some pics of setup.
Any ideas of what could be wrong would be much appreciated.
I'm no electrician (thankfully) - but going on my personal experience with my installation, and working through similar symptoms, I'm inclined to say this sounds very much like an EARTH problem which plagued me. I could well be wrong but might be a good starting point.
Note: This is my personal opinion based on my personal experience with a similar issue on my personal DB/Inverter hookup. had to put that in because sure enough, there will be people flaming in a bit.
Last edited: