A while ago I had another idea which is unfortunately flawed, but maybe it sparks something else.
I thought of bonding the input and output neutral. Since the output floats I am pretty sure you can bond the output neutral to the input and it also takes care of the grounding problem both on batteries and on Eskom. Current won't flow in the 'house' neutral when running off batteries because that is not part of the closed electrical circuit. The only problem I can think of is when your mains trip - then your house neutral is not bonded to earth any more and when the inverter kicks in you sit with the floating neutral problem again.
Maybe my studies/memory is letting me down here, please shoot holes as required![]()
That sounds like the best solution to date. My main switch only disconnects Live, so I will not have the floating Earth issue described here if the main switch trips.
Technically this must work without a problem in all scenarios:
1) Eskom is available and the inverter input is internally switched to the inverter output by means of a relay. That means that the input and output neutrals are bonded inside the inverter. There is also a bond between Neutral and Earth on the input of the inverter - that bond would be before the main ELR and since the Neutral in and Neutral out is bonded inside the inverter, there is a bond between Neutral and Earth on the inverter output as well.
2) Eskom is unavailable or PV power supplies the load or both, in the case of a true hybrid (e.g. infini). You create a Neutral Earth bond on the inverter output to prevent a floating earth and to ensure that the ELR on the inverter out functions properly. By creating a bond between Neutral and Earth on the inverter output and since the Neutral Earth bond on the inverter input is still in place (the Neutral Earth bond before the main ELR) and the inverter input Earth and output Earth is connected in the installation, you are actually bonding input Neutral to Output Neutral on the inverter.
In 1) above and when you create the N-E bond on inverter output in 2) above you actually have the inverter input and inverter output Neutrals bonded in both situations and by bonding them permanently you do not have to bond the Neutral and Earth on the inverter output only when Eskom is unavailable.