Most people houses idle under 1000wFar too much overkill.
6mm is fine, depending how much current you'll be pushing. If 5kw, 6mm is plenty fine.
Sounds like this will mostly be for load shedding vs generation.
i.e. 5kw inverter + batteries, mostly charged by Eskom. The 2 panels are going to be relatively worthless output wise. Maybe 1KW at best peak output (2 x 500-600w panels)., or 3-5kWh/ day summer, 1kWh/day winter.
2 x 5kWh batteries will be in the 50k + vat range.
3KW - 5KW inverter thats approved will be in the 20k +vat range.
Panels - 3k each ish, I'm not sure I'd bother with panels even, its almost not quite worth it.
With 2 panels, its probably not worth the initial extra cost. Yes, they'll help, but barely.Most people houses idle under 1000w
So any amount of panels will help recoup inverter /battery costs
No panels it is just an expense

Op has space for 2 panels.In my opinion the idle use panels cover roi faster
ie if you have 10kw of solar
And use 5kw of battery/load every 24hrs
Having the extra panels doesn't affect roi
So the few panels would be contributing 100% of their output to roi
Sub-zero temps should also be avoided for the battery, so hopefully there is enough heat generated inside during winter, or else the battery won't charge below 0 degrees.My idle power is about 300 watts at night, and probably at 600 to 800 watts in the day time. (Not going to move any heavey loads, so no geyser, oven over).
I know that the ROI will be like 10 years, but it is more a case of combatting loadshedding and other power issues. Myself and my wife work from home 80% of the time, so power is really key for us.
I do like the idea of doing a 5kw unit with external MTTP.
I'm up in Joburg, so dont have the humidity issues as in Cape Town. A ducted fan, to pull air into the hut, and expel will work. Will install seperate panel fans to gently flow air over the inverter, but wont push outside air direcrly over it.
All the feedback has been great, and I have to get over the hurdle with the body corporate, but that will have to wait for a bit.
With 2 panels, its probably not worth the initial extra cost. Yes, they'll help, but barely.
Looking at around 2-3 years before they start making a financial benefit. (assuming prices escalate YoY for power). I'd add, but they're minimal assistance. Better off saving that money initially, and buying decent equipment that will last you, vs going cheaper on all.
The other thing is good luck getting panels.
Earilest is mid April, some delayed till June.
View attachment 1491917
That would be segen, dealer side ex. vat pricing, as i mentioned in the thread.What is this site again?
6mm surfix gives you 34amps max without any correction factors ,that would be around 8 kw .dependant on temp ,buried,open,horizontal or vertical ,in a roofspace or does it see the sun and distance.Most people houses idle under 1000w
So any amount of panels will help recoup inverter /battery costs
No panels it is just an expense
And the cable thickness matters on bypass feature
ie as long as his load won't exceed the 6mm it may be fine
Not sure but he is most likely going on smallest armoured cable available
No idea what the smallest armour cable is just being devils advocate
10mm squared will give you around 5.5kw with a 220v single phase cable ,thats with a virtual worst case scenario power correction built in .but it still depends on how the cable is installedNot too far. Cable run will be about 20m. Will do a 10mm2 armoured cable, but that will be determined by the electrician.
Why would this have an effect?6
6mm surfix gives you 34amps max without any correction factors ,that would be around 8 kw .dependant on temp ,buried,open,horizontal or vertical ,in a roofspace or does it see the sun and distance.
it can drop by a factor of around 0.6 .sometimes as low as 0.4 .safe is 0.6 in any install it also allows a wee bit of headroom .
effect of correction factors there are many .any cable over 30deg c is allready penalised .voltage drop over distance .some wiseasses try use multicore cable .illegal .some use 3phase cable ,load capacity is reduced .220v single phase cable is very specific .harmonics can kill a cable .cables degrade rapidly if not suitable for the application .if your cable says 30amp times it by 0.6 and you should be safe .Why would this have an effect?
Say what now?10mm squared will give you around 5.5kw with a 220v single phase cable ,thats with a virtual worst case scenario power correction built in .but it still depends on how the cable is installed

H andV ,ive never asked why i just follow the regs ,ill look for you when i get a chanceWhy would this have an effect?
add in a correction factor of 0.6 and what do you get .how can you give advice without knowing the install ,are you even a certified electrician to be giving cable advice ?Say what now?
Single phase 10mm should be in the 70-80a range @ 220v., that would be about 15KW carrying capacity.
Even with a correction factor of 0.6, I still get 9KW.w
add in a correction factor of 0.6 and what do you get .how can you give advice without knowing the install ,are you even a certified electrician to be giving cable advice ?