2525252525
Expert Member
- Joined
- Apr 2, 2018
- Messages
- 1,844
- Reaction score
- 2,038
This is perfect, thanks, I'm going to staple an electrician who can issue COC's business card to it, else they can remove these things from the premises.Herewith some guidelines and requirement to connect a generator safely and legally to your premises
Connecting any unauthorised power source directly into any point of electrical wiring without a changeover switch is illegal and dangerous because of so-called “back feeding” which, by definition, means supplying power back into the grid when the grid is down. This must be avoided at all cost as the voltage fed back into the lines poses an electrocution hazard for utility workers and others who may not know that the line is charged.
Connection of any alternative power supply must comply with SANS 10142-1 Annexure S Emergency power installation configuration.
Never use a plug-to-plug cable to connect the generator to a socket outlet. Many generators are supplied with plug-to-plug cables, but their use is strictly forbidden as it provides no earth leakage protection.
Should the utility power be restored while the main circuit breaker is not switched off, the generator may be damaged or the entire system may be burnt, causing fire hazard.
While the main supply is not available, the generator will send power back into the main cable. This may overload the generator and shock electricians working on repairs on other power lines
Use a registered person in accordance with the Electrical Machinery Regulations to do the electrical installation. The registered person can be an installation electrician (IE) or master installation electrician (MIE) registered as a contractor with the Department of Labour. The registered person must issue a Certificate of Compliance upon completion of the installation.