I thought this may be useful to others.
I've completed an entire build, including wiring up my apartment with backup power (I live in Cape Town).
My equipment:
Backup system:
Inverter: Cotek SK1000-224
Motivation: There is plenty of info around about this inverter but essentially it is UL listed which is very hard to get. The product is built for industrial settings, it has high efficiency, high surge rating and very high quality output. During my testing the most powerful item I tested on it was a 980Watt Robi Angle grinder which ran without issues (startup had a momentary overload light show).
Cost: R3000 from eBay (lucky find)
Batteries: 2x Excis 12v 102Ah battery
Motivation: Really this was easily available from Makro. I don't recommend these batteries. I already paid for them so I'm staying with them for now but you can do better!
Cost: R1700 each from Makro
Charger: 2x Noco Genius G7200UK 7amp smart lead acid battery chargers
Motivation: There is a lot of information available about battery chargers. What I quickly learned was that if you want to have any hope of your batteries surviving a decent amount of time, you need smart battery chargers you can leave on 24/7 and not worry about over- or undercharging. I also have a CTEK charger and on my Oscilliscope (yes I have one), both charge with the same algorithm, so overall I think I got a good deal.
Cost: R800 each from Amazon.co.uk on special (R2000 total with shipping using Postbox courier to SA).
Power cables: 50mm^2 wire from Voltex in Cape Town + 10mm lugs.
Cost: Power cable is R71 a meter, R7 a lug. I bought 2 meters.
Custom modifications:
This is an inverter, it doesn't have a change-over switch (Automatic or otherwise) and it doesn't have an automatic turn on. Additionally during my testing I found that leaving it turned on consumed too much power.
Automatic switch over: I bought a Magnecraft 3 Pole, Double Throw 15 amp relay with a 240v coil from Amazon.com
Motivation: 3 Pole means that you can connect 3 wires. Double throw means it has two positions. So you have a switch that has two positions (on/off), each with three wires (live + neutral + earth for each position). The switch is turned on by 240v AC (normal wall power). So that means you can switch between Eskom (Live + Neutral + Earth) and Inverter (Live + Neutral + Earth).
Cost: Approx R300.
How well does it work? I think I should make a video and show on my Oscilliscope also, but essentially, with a light bulb there is a slight dim. Even on my APC I get a slight dim. You can hardly tell that you are switching over, it is very quick. On my Oscilliscope it takes about 1 AC cycle.
How did I wire this:
In short, do not wire this into your DB board. The great SABS safety loop hole is that you can wire anything from a plug. So as long as your wire this from a plug it is 100% safe. You wire a normal plug so that the live and neutral connect to the relay coil wires. Additionally the live + neutral + earth wire to the Normally Open contacts.
Your inverter has a plug coming out and you wire the live + neutral + earth to the Normally Closed contacts.
Wire your output (which should go to a multiplug or something) to the common contacts on the relay (again live + neutral + earth).
DO NOT SKIP THE EARTH on ANY contacts!
Plug in the Eskom plug and you should hear a click and your multiplug will already output power (unless there is load shedding).
Plug the other outlet into your Inverter.
How to auto-turn on your inverter:
All inverters have switches, so that makes it real simple. I bought a Single Pole Double Throw 240v AC coil relay from Communica for R60. That means it takes 240V from the plug and turns on a relay. I wire the power switch so that the on wire is wired to common and then the normally closed contact goes to the switch.
This means my inverter will only switch on if:
1) It is not plugged (the relay) in OR Eskom power is off
2) The Inverter on switch is on (I didn't remove that switch I simply added a second switch in line)
How well does this work? The relay has a 10ms switch time, it is so quick I can't even hear it click over the click of turning on the plug. It works incredible well. When Eskom power goes off my inverter switches on.
How did I wire my DB?
The truth is I only care about my house lights. All my plugs stuff I just run straight from the multiplug I mentioned before (or run leads). This is to avoid any legal issues with tampering with an electrical installation.
So how did I wire my lights?
Firstly my apartment has 3 phase. In Cape Town old houses and apartments have 3 phase. It is just how it is. So my lights are on a single phase and they aren't wired through a earth leakage.
All my lights run from a single 10 amp breaker.
I bought a CBI 2 pole 10 amp breaker before this I had a single pole.
Cost: R250 from RG Jack and Son in Cape Town
Ideally my lights should also go through a earth leakage after the 10amp breaker, but I am waiting on a 3 phase earth leakage and will then use the single phase earth leakage that was begin used on *some* of my plugs (yep my install is old an dodgy, they left some plugs off the EL, ouch)
I wired the light wire straight from cable that came into the box into the 2 pole breaker (so I can still switch off lights at the DB Board). Then I bought a solid core SABS rated cable into the box and it goes straight into the 2 pole breaker at the top. The other end plugs into the multiplug. It is labelled as having backup power on my DB board.
So my lights are wired from either my house plugs or inverter VIA a plug. As far as I can tell this should be up to code, especially if I run my lights through a EL.
The ground wire goes straight through to the plug (not DB board ground). This allows it to ground to the inverter or house depending on which supplies the power. There may be a ground interrupt but at the same time, live and neutral are also broken so I think it is overall safe. (Comments welcome on this)
Final words:
I'll update with some pics if there is more interest!
Drop some comments.
Some of this stuff I based on my own knowledge, SABS documents, etc. This was a lot of work in terms of research and comments welcome if you know better. I would love to share some knowledge on this and don't mind getting some pics with a decent how to. Overall you can build a pretty impressive setup for relatively low cost. (Think I've paid about R10k so far)
Let's get the ball rolling on knowledge sharing please
I've completed an entire build, including wiring up my apartment with backup power (I live in Cape Town).
My equipment:
Backup system:
Inverter: Cotek SK1000-224
Motivation: There is plenty of info around about this inverter but essentially it is UL listed which is very hard to get. The product is built for industrial settings, it has high efficiency, high surge rating and very high quality output. During my testing the most powerful item I tested on it was a 980Watt Robi Angle grinder which ran without issues (startup had a momentary overload light show).
Cost: R3000 from eBay (lucky find)
Batteries: 2x Excis 12v 102Ah battery
Motivation: Really this was easily available from Makro. I don't recommend these batteries. I already paid for them so I'm staying with them for now but you can do better!
Cost: R1700 each from Makro
Charger: 2x Noco Genius G7200UK 7amp smart lead acid battery chargers
Motivation: There is a lot of information available about battery chargers. What I quickly learned was that if you want to have any hope of your batteries surviving a decent amount of time, you need smart battery chargers you can leave on 24/7 and not worry about over- or undercharging. I also have a CTEK charger and on my Oscilliscope (yes I have one), both charge with the same algorithm, so overall I think I got a good deal.
Cost: R800 each from Amazon.co.uk on special (R2000 total with shipping using Postbox courier to SA).
Power cables: 50mm^2 wire from Voltex in Cape Town + 10mm lugs.
Cost: Power cable is R71 a meter, R7 a lug. I bought 2 meters.
Custom modifications:
This is an inverter, it doesn't have a change-over switch (Automatic or otherwise) and it doesn't have an automatic turn on. Additionally during my testing I found that leaving it turned on consumed too much power.
Automatic switch over: I bought a Magnecraft 3 Pole, Double Throw 15 amp relay with a 240v coil from Amazon.com
Motivation: 3 Pole means that you can connect 3 wires. Double throw means it has two positions. So you have a switch that has two positions (on/off), each with three wires (live + neutral + earth for each position). The switch is turned on by 240v AC (normal wall power). So that means you can switch between Eskom (Live + Neutral + Earth) and Inverter (Live + Neutral + Earth).
Cost: Approx R300.
How well does it work? I think I should make a video and show on my Oscilliscope also, but essentially, with a light bulb there is a slight dim. Even on my APC I get a slight dim. You can hardly tell that you are switching over, it is very quick. On my Oscilliscope it takes about 1 AC cycle.
How did I wire this:
In short, do not wire this into your DB board. The great SABS safety loop hole is that you can wire anything from a plug. So as long as your wire this from a plug it is 100% safe. You wire a normal plug so that the live and neutral connect to the relay coil wires. Additionally the live + neutral + earth wire to the Normally Open contacts.
Your inverter has a plug coming out and you wire the live + neutral + earth to the Normally Closed contacts.
Wire your output (which should go to a multiplug or something) to the common contacts on the relay (again live + neutral + earth).
DO NOT SKIP THE EARTH on ANY contacts!
Plug in the Eskom plug and you should hear a click and your multiplug will already output power (unless there is load shedding).
Plug the other outlet into your Inverter.
How to auto-turn on your inverter:
All inverters have switches, so that makes it real simple. I bought a Single Pole Double Throw 240v AC coil relay from Communica for R60. That means it takes 240V from the plug and turns on a relay. I wire the power switch so that the on wire is wired to common and then the normally closed contact goes to the switch.
This means my inverter will only switch on if:
1) It is not plugged (the relay) in OR Eskom power is off
2) The Inverter on switch is on (I didn't remove that switch I simply added a second switch in line)
How well does this work? The relay has a 10ms switch time, it is so quick I can't even hear it click over the click of turning on the plug. It works incredible well. When Eskom power goes off my inverter switches on.
How did I wire my DB?
The truth is I only care about my house lights. All my plugs stuff I just run straight from the multiplug I mentioned before (or run leads). This is to avoid any legal issues with tampering with an electrical installation.
So how did I wire my lights?
Firstly my apartment has 3 phase. In Cape Town old houses and apartments have 3 phase. It is just how it is. So my lights are on a single phase and they aren't wired through a earth leakage.
All my lights run from a single 10 amp breaker.
I bought a CBI 2 pole 10 amp breaker before this I had a single pole.
Cost: R250 from RG Jack and Son in Cape Town
Ideally my lights should also go through a earth leakage after the 10amp breaker, but I am waiting on a 3 phase earth leakage and will then use the single phase earth leakage that was begin used on *some* of my plugs (yep my install is old an dodgy, they left some plugs off the EL, ouch)
I wired the light wire straight from cable that came into the box into the 2 pole breaker (so I can still switch off lights at the DB Board). Then I bought a solid core SABS rated cable into the box and it goes straight into the 2 pole breaker at the top. The other end plugs into the multiplug. It is labelled as having backup power on my DB board.
So my lights are wired from either my house plugs or inverter VIA a plug. As far as I can tell this should be up to code, especially if I run my lights through a EL.
The ground wire goes straight through to the plug (not DB board ground). This allows it to ground to the inverter or house depending on which supplies the power. There may be a ground interrupt but at the same time, live and neutral are also broken so I think it is overall safe. (Comments welcome on this)
Final words:
I'll update with some pics if there is more interest!
Drop some comments.
Some of this stuff I based on my own knowledge, SABS documents, etc. This was a lot of work in terms of research and comments welcome if you know better. I would love to share some knowledge on this and don't mind getting some pics with a decent how to. Overall you can build a pretty impressive setup for relatively low cost. (Think I've paid about R10k so far)
Let's get the ball rolling on knowledge sharing please