ABB XT1N 160That cannot be true.
Datasheet says "Shunt Trip Circuit Breaker sized to suit max current", so a 100A breaker on a 200A battery would not make sense.

Rated current: 100A
I'm open to correction. I had the same q for FW... it's a 1c 200Ah battery, it should be able to do max 200A. I know ratings on breakers are for test purposes, but even 160A continuous is less than the 200 the battery is capable of.
What's confusing is that the spec sheet for that breaker has max current as variable - assuming dependent on the breaker you buy, but it still says max 160a continuous and 100A rated (I.e. tested).
To add to the confusion, the battery is rated to be paired with up to 10kw inverter. That demand is already going to hit 200A if I'm not mistaken... but there you go. A question for the FW fundis.
... how else is one meant ot interpret this: