Just a followup, I see a drop in the supposed output but a lot of our stuff is quieter now including I assume geyser so it makes sense that figure dropped from what you said as I would not expect the panel output to drop as the sun rose higher. So it will not show excess unless I was exporting to grid? Only what the home can draw?Usually your solar array only creates power when there is a load ie battery charging, ups load, etc
You only know how much solar power is available when the mppt tries to power loads.
You won't see an array availability with no load
this tracks with how it all should work. hope they manage to sort your cablingJust a followup, I see a drop in the supposed output but a lot of our stuff is quieter now including I assume geyser so it makes sense that figure dropped from what you said as I would not expect the panel output to drop as the sun rose higher. So it will not show excess unless I was exporting to grid? Only what the home can draw?
CorrectJust a followup, I see a drop in the supposed output but a lot of our stuff is quieter now including I assume geyser so it makes sense that figure dropped from what you said as I would not expect the panel output to drop as the sun rose higher. So it will not show excess unless I was exporting to grid? Only what the home can draw?
Which model and how many batteries do you have? Generally nothing wrong with increasing the grid charge amps, just make sure you're at or lower the max charge for the batteryHello friends..
Asking a question for a friend here
Noticed the charging is working REALLY well from PV.. but from Grid, eh not so much.
I have it set as follows:
View attachment 1498331
Any danger in raising the Max grid charge current to something a bit more spicy ?
Say.. 60Amps.. or more ...
It does charge, but only at the mentioned rate of 40 AmpsIt won't magically start it charging. What battery does your friend have? Max charge current depends on the battery.
12 Kw 3 Phase Deye and as mentioned aboveWhich model and how many batteries do you have? Generally nothing wrong with increasing the grid charge amps, just make sure you're at or lower the max charge for the battery
40a at 48v is about 2000wHello friends..
Asking a question for a friend here
Noticed the charging is working REALLY well from PV.. but from Grid, eh not so much.
I have it set as follows:
View attachment 1498331
Any danger in raising the Max grid charge current to something a bit more spicy ?
Say.. 60Amps.. or more ...
Yeah then you should be good to increase. 21kwh gives you a mac 0.5C of approx 10kw = 200amps or so. Limits will be enforced by the BMS and cablingIt does charge, but only at the mentioned rate of 40 Amps
He has 1x 7.4Kw SMD and 1x 14.3Kw SMD
12 Kw 3 Phase Deye and as mentioned above
1x 7.4Kw SMD and 1x 14.3Kw SMD
So raise it to 100 Amps should be safe ?Yeah then you should be good to increase. 21kwh gives you a mac 0.5C of approx 10kw = 200amps or so. Limits will be enforced by the BMS and cabling
100amps should be safeSo raise it to 100 Amps should be safe ?
Turned out the electrician connected the CT to pins 3&4 (CT1) instead of pins 5&6 (CT2). I fixed that and everything works correctly now.
Hmm so then I assume they using one of the cat5 pairs then to run to inverter. Pretty sure it's clamped correctly as that's exactly what the main elec told the other so more than likely is wrong on on the inverter then if this is the issue.CT is just two wires, no connector. Pins are different for 5 and 8kw units.
![]()
Using a CT Coil
Basic understanding of using a CT coil it is used to control the export or import of the power from the grid this is very important and care must be taken when using CT, to ensure it is wired correctly Note Black is NEUTRALwww.sunsynk.org
Interesting, I have 125 in my breaker so can do 100 with no issues. Battery is also rated for 50a and I have 2. BMS also targets 100 whenever possible100A is the rating of the breaker on my FW 10/8 battery. I'd say that's a bit close to the edge.
Same cableBut help me understand this. The inverter is wired to certain circuits for load. This works if the inverter is in mains failure. I assume the inverter has a high rated input feed and the load is the output but if sending to the board, how does it send power to non load circuits, ie balance of the db, is there another cable?
Then in theory, it could be supplying the house but just not reporting it? Trying to understand how the "backflow" works.Same cable
But help me understand this. The inverter is wired to certain circuits for load. This works if the inverter is in mains failure. I assume the inverter has a high rated input feed and the load is the output but if sending to the board, how does it send power to non load circuits, ie balance of the db, is there another cable?
Your main eskom wire comes in and gets split (parallel seperation): 1 goes to inverter and 1 goes to non essential db.Kosmik said:Then in theory, it could be supplying the house but just not reporting it? Trying to understand how the "backflow" works.