So I'm just getting into playing around with my SDR a bit more.
I bought a discone antenna and now a 6m mast. The mast I'll mount against the chimney, so it will be about 8m high.
Nearby is a lightning conductor, 15m high.

Would the following make sense.
Ground the mast using it's own earth spike.
Ground the outer shielding of the coax to the same spike.
Then I was thinking of adding an earth strap between the mast and the lightning conductor?

I'm just a bit paranoid of lightning after we took a direct hit to our house recently.
 
So I'm just getting into playing around with my SDR a bit more.
I bought a discone antenna and now a 6m mast. The mast I'll mount against the chimney, so it will be about 8m high.
Nearby is a lightning conductor, 15m high.

Would the following make sense.
Ground the mast using it's own earth spike.
Ground the outer shielding of the coax to the same spike.
Then I was thinking of adding an earth strap between the mast and the lightning conductor?

I'm just a bit paranoid of lightning after we took a direct hit to our house recently.
What conductor are you using for grounding the mast?


 
What conductor are you using for grounding the mast?


I'll get some 10 AWG wire to attach the mast to the spike.

I wasn't going to use an inline surge protector as I figured I'd disconnect any devices when there's a storm around.
But thinking about it, even if disconnected the surge running down the coax into the house is a fire risk.
 
I'll get some 10 AWG wire to attach the mast to the spike.

I wasn't going to use an inline surge protector as I figured I'd disconnect any devices when there's a storm around.
But thinking about it, even if disconnected the surge running down the coax into the house is a fire risk.
Yeah, true. Not sure about in-line coax surge arrestors… does such a thing exist?
 
Yeah, true. Not sure about in-line coax surge arrestors… does such a thing exist?
They do, but I was just reading about them and they aren't recommended due to the possible signal loss.
So as far as the coax goes they recommend grounding the outer shield.

The reason I want to connect the mast to the lightning conductor is I've read never have 2 separate earthing points as it can cause a difference in potential electrical build up.
 
May be an image of lightning and text that says LIGHTNING PROTECTION @mbsarchi பய ROD ROD CONDUCTOR t EARTH ISOLATION POINT EARTHING
 