~85+~140 => ~225? Close to 220V - coincidence?
No coincidence, the differential between L and N is correct, but the offset from earth is what bothers me.
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
~85+~140 => ~225? Close to 220V - coincidence?
I've also installed the Axpert KS-2KVA with 2 x 102Ah Deltec deep cycle batteries in series. Does its thing quite admirably.
This thread got me thinking, last night I measured the AC voltage between Earth & Live and Earth & Neutral, while operating in battery mode (isolated inverter input with DP isolator). Got ~85V between Earth & Neutral and ~140 between Earth & Live on the output. Measured with a DMM.
Does this imply that the neutral is floating, i.e. not bonded internally? Do I need better test equipment? Do I need to/can you bond the neutral and earth on this unit?
On the hunt for this also and the best prices/range I'm finding so far are acdc dynamics www.acdc.co.za - not sure if anyone else has better ideas to share I would also appreciate more leadscan anyone tell me where I can have a rack or enclosure made?
Does this imply that the neutral is floating, i.e. not bonded internally? Do I need better test equipment? Do I need to/can you bond the neutral and earth on this unit?
_______________________________________________________________________________________
Whats the answer to that?
It looks like Chris has tied his neutral to earth, as described in one of the earlier posts. Just need to verify that his Inverter is also an Axpert unit...
It looks like Chris has tied his neutral to earth, as described in one of the earlier posts. Just need to verify that his Inverter is also an Axpert unit...
Yes, don't want to try and do that and smoke it... :wtf:
There's absolutely nothing wrong or dangerous with doing this (as long as your inverter is not behind a E/L). I need to run out in a few minutes, so don't have the time now. I'll post something about this (and why) a bit later. Neutral + Earth, must be bonded. Hint - look at this from a generation point of view, not a distribution point of view. When you are in Battery / PV mode, your inverter is a GENERATOR.


Also, has anyone used the batteries I've ordered and can anyone tell me where I can have a rack or enclosure made?
Thank you.
There's absolutely nothing wrong or dangerous with doing this (as long as your inverter is not behind a E/L). I need to run out in a few minutes, so don't have the time now. I'll post something about this (and why) a bit later. Neutral + Earth, must be bonded. Hint - look at this from a generation point of view, not a distribution point of view. When you are in Battery / PV mode, your inverter is a GENERATOR.
Only risk I can see is that the UPS itself isn't E/L protected. So if something fails in the UPS (which has a metal case), you could shock yourself?