My house is so energy efficient now that i wanted to use the existing EL behind the Axpert, and slap the 32A in before the Axpert between it and Eskom, since the Axpert is grounded to the Earth on the panel too. (Reason, should I have a short somewhere , the EL does disconnect and the axpert takes over on battery power, could be quite expensive error there.)
Here we go again...
A BREAKER will trip when there is a SHORT, a EARTH LEAKAGE will trip when there's an Earth Leakage - those are two fundamentally different error conditions.
You will need to have double pole BREAKERS on your supply, and load through the Inverter
Your Neutral BEHIND the Inverter, MUST be bonded to ground. If your supply is connected behind your Earth Leakage, your Earth Leakage WILL trip as soon as the inverter operates in bypass mode.