ADVICE ON SIZING PV PANELS TO AXPERT INVERTER
Hi all
I am a total newbie to this forum and have literally spend hours reading through all the threads and comments over the past few months. I am now in the final stages of acquiring components for my systems to power my house off solar during the day, and off batteries during the night, but I need advice please, as I am getting very different responses to some issues.
1. I have already bought one Axpert 5kva inverter(48v) and this will be wired into my DB Board. I will add-on another 5kva unit and run it in parallel as to be able to increase my total PV input to the maximum of 6kw.
2. I've already bought 4 12v 260ah Omnipower solar batteries and this will provide me with battery backup during loadshedding for now, and maybe enough to carry me through the night (30% DoD), as I've calculated my average nightly use to be in the region of 600w-700w. If I add the other Axpert it will also have the same battery bank as above
3. My DB board will be split into various sections, as I am planning to remove my garage from running from the inverter fulltime. I have lots of woodworking machinery, grinders and cutters as well as welding equipment which I do not think would be wise to run through the inverter. I am however considering (if possible) having my garage on a manual changeover switch which would enable me to run normal lights and plugs through the inverter during light use, and manually switch back to Eskom should I start working with my machinery over weekends. Any ideas or recommendations if this would be a viable idea?
4. My scullery's plugs running serving the dishwasher, auto washing machine and tumble dryer I am also planning to still run from Eskom power. I am unsure if these machines can be run effectively through the inverter setup, but if it will be mostly run during the day, so it would be nice to run this while my PV is supplying the power. Anyone having some comment on this?
Lastly, and this is where I really need advice, as I am now in the final process of going ahead and buying the solar panels.
I am looking at the ReneSola Solar Panels as they are priced well, but I am having some issues sizing my panels to correctly function with the Axpert. The Axpert is limited to 3000W maximum PV input, and a maximum PV of 145vdc, with a MPPT operating voltage of between 60vdc and 115vdc. These panels will be installed on my Garage's roof, which is facing north, and I have space for at least 21 panels for now. I am in Centurion and my garage is getting full sun during the day
I am however confused on whether to use the STC values of the panels for working out string and panel combinations, or rather using the NOC values.
I am considering the 250W panels, providing Voc(STC) of 37.4v, and max power of 8.31amps (STC). If these are the values to be used instead of NOCT values, I can effectively have 12panels to each inverter, set up in 4 strings of 3 panels each. This will give me a max of 3000w(STC) with 112vdc which is within limits of the Axpert, with maximum 33.24amps. Am I correct in my calcs?
However, if I look at the NOCT values of the same panels, using the same string combinations as above, max Watts drop to 2220 (185w per panel), with 105vdc(35v per panel) at only 26,28Amps (6.57a per panel)
So can someone please comment on whether this would be sufficient, or can I maybe look at adding one more panel to each string as the NOC values are more realistic and would still maybe leave me within the limits of the Axpert.
I would really appreciate some feedback and any other comments to my planned system as I want to be sure that my system is configured to the maximum efficiency.
Thanks in advance