TheChamp
Honorary Master
Firstly, the recommended minimum Ah for a 48V model is 200Ah, you will see that on your manual when going through it, it will work with 105Ah but you might experience issues.
Program
01 Should be left on default, 01 Uti
02 Set it to 20A
03 Set to UPS
04 Set to enable SEN
05 Not sure if your batteries are flooded or AGM, choose accordingly.
06 Enable
07 Enable
08 N/A or default
09 Default
11 Set to 20A
12 N/A Default
13 N/A Default
16 Utility first CUt
18 to 25 default
26 to 27, refer to battery specs or default
29 Set to 48V
31 to 38 default.
Program
01 Should be left on default, 01 Uti
02 Set it to 20A
03 Set to UPS
04 Set to enable SEN
05 Not sure if your batteries are flooded or AGM, choose accordingly.
06 Enable
07 Enable
08 N/A or default
09 Default
11 Set to 20A
12 N/A Default
13 N/A Default
16 Utility first CUt
18 to 25 default
26 to 27, refer to battery specs or default
29 Set to 48V
31 to 38 default.