The whole system needs to be re-assessed. These are fine for low amp, thin cord appliances, but not 4kW heaters and 220A-output welding machines with high amps and heavy, stiff cords. I'd love to see houses built with two types of sockets, and if that's the case then fine, use this as the low amp socket, but this is not a one-size-fits-all plug. Wire these sockets with 1mm² cable and put a 10A breaker on them, but you also need a standard for high amp appliances. IEC 60309 is fine, but make it a standard, and offer guidance to architects and developers. Otherwise stick with what we've got.
And for those saying, "but these are 20A". Go for it, wire up a 2.5mm² cord to one of these puppies and see how well those 4mm plastic pins hold it in the socket. I use 4mm² H07RN extension cords (for volt drop over 100m, still 20A) and I struggle to wire that into a normal SA plug. Good luck using one of these.