Thanks, happy to assist - let us know if you pick up somethingSure I get that, I haven’t logged with support yet, it’s just something I’ve noticed the last few days. I’ll continue monitoring and if it gets worse I’ll log a ticket.
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
Thanks, happy to assist - let us know if you pick up somethingSure I get that, I haven’t logged with support yet, it’s just something I’ve noticed the last few days. I’ll continue monitoring and if it gets worse I’ll log a ticket.
Not seeing any issues this side, likely localised. Area and FNO?Down again?
Thanks!View attachment 1868799
Vumatel Network Maintenance in your area, OLT replacement. ETR 08:00 05/12/2025
Thank you for the feedbackEvening all, apologies for the late reply. We had a team at Teraco until late this evening, and a configuration change led to a short outage just after 18:05pm, services were fully restored by 18:11. Apologies for the inconvenience caused.
We're still completing the post mortem on this morning's outage. Thank you for your patience and continued support.
Morning, apologies missed this one. Yes we are aware of this one. It's been a bit hit or miss with NTT (Vodafone's preferred upstream). Let me sit with the team and review the trail, including with the B side ISP and see what can be done here. Thanks for your patience on this one.@websquadza hi, I've been struggling with this ticket for a while (513980). I understand that it's limited to a particular route, and that is looks like multiple ISPs involved. but any more we can do?
awesome feedbackThank you for your patience on regarding Thursday's outage, we were awaiting feedback from Teraco on the cause of Thursday's outage - see below our Post Mortem:
On Thursday 4 December 2025, at around 11:00 we experienced an outage impacting our Teraco Isando core. Our investigation showed that a B-feed power circuit in our rack had tripped, causing two critical switches (Spine-01 and Leaf-02) to lose power. Both devices had unflagged A-feed vulnerabilities—Spine-01 had a failed PSU, and Leaf-02 had a loose A-feed power cable—so when the B-feed dropped, both switches went completely offline, isolating the remaining leaves and taking the fabric down.
Teraco has since completed their own investigation and confirmed that a fault on a PSU on a dual-corded device caused a circuit breaker trip on one of the PDUs, resulting in the feed loss and multiple devices powering down. Their technicians restored the breaker and verified the affected PDU’s stability once the device was reconnected.
Once services were restored at 11:51, our team remained onsite for the rest of the day to fully rewire the rack with new A/B power cabling, reseat all connections, replace our management stack, add full console access, and introduce our second spine into production for more resilient HA (this had been planned). Teraco is also installing an additional independent A+B rail for us to further strengthen power resilience with A1/A2, B1/B2 rails.
A tough outage, but a valuable one—we’ve addressed every contributing factor and implemented structural improvements to prevent a repeat. Thanks to everyone for the patience and support while we worked through it.
Merry Christmas, wishing you and your loved ones a special day!

Morning I see our team did reply on your ticket. Logged with Vuma, seems to be a line fault. Will ask them to check in again.Vuma trenched offline East Rand
It supposed to terminate 29/12/25
Are you on holiday. Logged ticket #905869. No response from the WEB.
Likewise, for you too! Looking forward to it!Thank you
Hope 2026 is a great year!
Will be bugging you nice and early in the year![]()
Drop me a PM with their details so we can link the lead to you as an affiliate. Thank you for the recommendation!@websquadza I recommended you guys to a friend & he signed up, don’t disappoint![]()