8kw split over 3 phases would probably explain why it was discontinued, 12 kw a much better option.
South Africa’s biggest forum. Discuss, discover, and connect with thousands of members.
House is 3 Phase we only need 5kw and 12kw is about R20k more than 8kwIve only ever seen the 12kw version.
Is it a price thing or any other specific reason why you don't want the 12kw instead of the 8kw?
Do you have any 3 phase equipment? Easiest is often to just put everything back on one phase. Then you can use a single phase inverter.House is 3 Phase we only need 5kw and 12kw is about R20k more than 8kw
I agree with this. If it's not needed then just use 1 phase.Do you have any 3 phase equipment? Easiest is often to just put everything back on one phase. Then you can use a single phase inverter.
Anyone know where I can get a 8kw 3 phase Sunsynk Inverter? Looking online seems only one shop - https://volocityenergy.com/products...JnPaQxjgGEowgeCCb7O5b3ij9g7HSMat5TVhh3OGWhNU0
Happy to buy direct from installer as well.
You set the SoC in the system work mode.I have a DEYE 8kVA single phase inverter with 2x Pylontech UP5000 batteries, no solar panels yet.
Is there a way to tell the inverter to only charge the batteries to say 80% SoC in order to save a little on the cycles?
The lowest SoC that I have seen during a 4-hour loadshedding stint was 54%, so I think I am safe starting at 80%.
Any merit in this approach?
By using the time of use table?You set the SoC in the system work mode.
YesBy using the time of use table?
450kwh of lithium batteries or AGM/GEL?
That is an INSANE amount of storage
I think there is a mistake there. Unless it's for 2 to 3 weeks of storage.That is an INSANE amount of storage
450kwh of lithium batteries or AGM/GEL?
Correction 14.3 + 7.4 kWHThat is an INSANE amount of storage
Lol. There's a pretty hefty difference between 450kWh and 21.7kWhCorrection 14.3 + 7.4 kWH
All Lithium setup
I mixed up my Ah and Kwh :'(Lol. There's a pretty hefty difference between 450kWh and 21.7kWh
Good thinking. The problem is that one can only control the charge from Grid and Genny, not solar.I have a DEYE 8kVA single phase inverter with 2x Pylontech UP5000 batteries, no solar panels yet.
Is there a way to tell the inverter to only charge the batteries to say 80% SoC in order to save a little on the cycles?
The lowest SoC that I have seen during a 4-hour loadshedding stint was 54%, so I think I am safe starting at 80%.
Any merit in this approach?
www.sunsynk.org
Whoops. Had my math malfunctioning a bit...21.7 @ 54v = 401.85Ah