So just a quick glance at the settings, from my understanding, for the inverter to fedback succesfully, two criteria are needed:
1. Detections draw from the grid so that the system is aware how much it can safely provide.
2. It must output at a higher voltage than the incoming grid to prevent draw from the grid.
Looking at the below when clicking grid
View attachment 1498603
It's showing zero grid and zero CT. Now and then there is a 10w on the grid but CT is flat zero. The LD I assume is the load circuit and that seems about right for what's running right now and I can see it fluctuate as things like my washing machine motor kick in.
Looking at the grid setting, it's configured to output at 230, which is LESS than my supply.
View attachment 1498605
I asked the sparkie originally if the inverter would be able to sense the grid voltage and adjust its output but this seems like it overrides that.
@Speedster can you shot those screens on yours? First is the grid and second is settings/grid settings.
The CT clamp is used for a number of things. It measures power coming in from the grid.
It measures and allows the inverter to maintain a small draw(configurable) when the inverter is running the non-essentials from solar/PV
It measures the grid export if that's set.
The inverter voltage is only used in islanding mode. It syncs with the grid voltage under other modes.