All things Sunsynk (Deye, Inge, etc...)

Can someone explain the SSEG requirement? Is application required even if you don't feedback to the grid - but still have a grid connected system?
If you generate through panels you must register in CoCT. Backup system only does not have to be registered.
 

Should register it just to be "safe"

"There is no charge to register EG systems. A fee will only be applied if you fail to register your system. Grid engineering studies will be done by the City for the proposed PV installation should these be required."

"Non-feed-in system
If you are installing a non-feed-in system (with reverse power flow blocking), you will remain on your current tariff. You will be able to connect your system from the day you receive your Commissioning Approval Letter."


If you generate through panels you must register in CoCT. Backup system only does not have to be registered.

I'm in Cape Town - but Eskom is our provider.

Asking because a neighbour sent me their quote with a R10k application fee to City of Cape Town - IF they choose solar panels, which now has me googling - because our electricity has nothingt o do with City of Cape Town.

Tried to download some of the docs from Eskom's site - but in true government style - 404s.

I initially thought the application was only if you feed back into the grid.
 
I'm in Cape Town - but Eskom is our provider.

Asking because a neighbour sent me their quote with a R10k application fee to City of Cape Town - IF they choose solar panels, which now has me googling - because our electricity has nothingt o do with City of Cape Town.
If you're with Eskom direct then you don't need to register with CoCT.

Eskom has their own SSEG registration but nobody actually does this, it's not a requirement for insurance (they only asked for COC) so I didn't bother with it, although I did attempt to figure it out - here is my post about it: https://mybroadband.co.za/forum/threads/sseg-registration-eskom-cape-town.1221019/
 
Stupid question - but why is this only a requirement if have panels?

What's the difference if I have a generator connected to the inverter? (or just the batteries) - surely its the same risk, the power will just run out quicker.
 
Stupid question - but why is this only a requirement if have panels?

What's the difference if I have a generator connected to the inverter? (or just the batteries) - surely its the same risk, the power will just run out quicker.
You're expecting some sort of rationality behind a south African government requirement... lol...
 
Stupid question - but why is this only a requirement if have panels?

What's the difference if I have a generator connected to the inverter? (or just the batteries) - surely its the same risk, the power will just run out quicker.
Actually you are required to get authorisation to connect a generator. And that is even more arduous as you need environmental and fire dept involved. I just don't know of anybody that has done it that way. But they say ignorance of the law is no excuse.
 
Thanks, I can't put the inverter in the garage as it has some dampness issues and it's also on the opposite end of the property far away from the DB.

1 option I have is to put the inverter in the lounge, directly behind the DB or in a sheltered and gated off courtyard area but then dust might become an issue and it's also a bit less secure.

I came across this thread where they added external fans to the side of the inverter but no reports of how it fares during summer: https://powerforum.co.za/topic/17423-my-sunsynk-8kw-silence-hack/
My 8kW is in the scullery just behind the kitchen. It is noticeable when the fans come on, but not so much that it is unbearable. If we are watching TV you hardly hear it. Sound like a vacuum running far away. I might add a door to the partition between the kitchen and the scullery later to block more noise. Also need to add an extractor fan to the ceiling as that part of the house can get hot.

I have 2x 120mm PC fans mounted on the inlet side, the blow into the existing fans. I left a small gap because I don't want to restrict the built-in fans. They are nowhere near as powerful as the built-in fans in terms of airflow though. I am using cheap fans with 43 cfm, but even looking at the more expensive ones they seem to max at around 60cfm. The built-in fans are 90mm I think. Each of my fans has a duct to reduce to the same size as the built-in fan. I think it helps the temperatures, but on a hot day where you are using a lot of power the fans will still come on a lot. This graph is from yesterday, max outside temp was 27C I think with lots of power being used during the day. Each sharp drop in temperature is where the fans came on. I just got a 3rd fan that I still need to install, think it will help a little bit to get more airflow through the inverter but the fans will still come on.
1682434410611.png


And over a couple of days:
1682434658093.png
 
Hmm,

Not sure if anyone else has experienced this.

Time of work set (in this particular instance to 70% - see screenshot).

0d47a0effd19349bc85d6851ad553466.png


I noticed that the inverter was happily pulling from the battery even though it was already sitting at 49% with a Loadshedding slot incoming.

Checking in SolarAssistant (in my alarmed state I forgot to take a screenshot I realised that even though my settings were as per the screenshot above, the 'Current Mode - Charge Below' value was sitting at 35%.

When I checked the inverter screen, this is what I saw:

47c75a48702849acf9360360ac6824b7.jpg


Couldn't figure out how to get everything back to 'normal' (ticking and unticking work mode didn't achieve anything) so I eventually 'rebooted' (switched house to mains, switch off batteries, switch off inverter).

Waited a couple of minutes, did the reverse of the above and blech! the screen showed grid unavailable.

Then had a brainfart and thought that if I switched off the batteries maybe it would 'kickstart' the grid connection - not one of my better moments.....

Anyhow, I'd forgotten to switch the bypass for the house back to Grid so there were howls of protest, disbelief and general gnashing of teeth as my family was plunged into darkness for the first time in weeks....

Quickly did the switch and got back to the Inverter to switch everything back on (the exact sequence is a bit fuzzy now).

Greeted with this message

842e1331197a3f61733f9cbcc7888b57.jpg


Rechecked everything, Grid Setting

096f82c2f5d5b9a84bd58fd9d36142c3.jpg


At this point I restarted everything again and hoped for the best (the 20h00 LS slot breathing down my neck).

This time the restart was successful and the inverter reverted to normal operation.

Now that the dust has settled, I'm leaning toward the 'Current Mode' setting not updating in line with the current 'work mode slot' value - it's most disconcerting and, in the current LS climate, makes me feel nervous about using the 'work mode' function.
 
Hmm,

Not sure if anyone else has experienced this.

Time of work set (in this particular instance to 70% - see screenshot).

0d47a0effd19349bc85d6851ad553466.png


I noticed that the inverter was happily pulling from the battery even though it was already sitting at 49% with a Loadshedding slot incoming.

Checking in SolarAssistant (in my alarmed state I forgot to take a screenshot I realised that even though my settings were as per the screenshot above, the 'Current Mode - Charge Below' value was sitting at 35%.

When I checked the inverter screen, this is what I saw:

47c75a48702849acf9360360ac6824b7.jpg


Couldn't figure out how to get everything back to 'normal' (ticking and unticking work mode didn't achieve anything) so I eventually 'rebooted' (switched house to mains, switch off batteries, switch off inverter).

Waited a couple of minutes, did the reverse of the above and blech! the screen showed grid unavailable.

Then had a brainfart and thought that if I switched off the batteries maybe it would 'kickstart' the grid connection - not one of my better moments.....

Anyhow, I'd forgotten to switch the bypass for the house back to Grid so there were howls of protest, disbelief and general gnashing of teeth as my family was plunged into darkness for the first time in weeks....

Quickly did the switch and got back to the Inverter to switch everything back on (the exact sequence is a bit fuzzy now).

Greeted with this message

842e1331197a3f61733f9cbcc7888b57.jpg


Rechecked everything, Grid Setting

096f82c2f5d5b9a84bd58fd9d36142c3.jpg


At this point I restarted everything again and hoped for the best (the 20h00 LS slot breathing down my neck).

This time the restart was successful and the inverter reverted to normal operation.

Now that the dust has settled, I'm leaning toward the 'Current Mode' setting not updating in line with the current 'work mode slot' value - it's most disconcerting and, in the current LS climate, makes me feel nervous about using the 'work mode' function.
Very weird, wonder if there was a frequency/voltage issue on the grid in your area and the system went out of bounds
 
My 8kW is in the scullery just behind the kitchen. It is noticeable when the fans come on, but not so much that it is unbearable. If we are watching TV you hardly hear it. Sound like a vacuum running far away. I might add a door to the partition between the kitchen and the scullery later to block more noise. Also need to add an extractor fan to the ceiling as that part of the house can get hot.

I have 2x 120mm PC fans mounted on the inlet side, the blow into the existing fans. I left a small gap because I don't want to restrict the built-in fans. They are nowhere near as powerful as the built-in fans in terms of airflow though. I am using cheap fans with 43 cfm, but even looking at the more expensive ones they seem to max at around 60cfm. The built-in fans are 90mm I think. Each of my fans has a duct to reduce to the same size as the built-in fan. I think it helps the temperatures, but on a hot day where you are using a lot of power the fans will still come on a lot. This graph is from yesterday, max outside temp was 27C I think with lots of power being used during the day. Each sharp drop in temperature is where the fans came on. I just got a 3rd fan that I still need to install, think it will help a little bit to get more airflow through the inverter but the fans will still come on.
View attachment 1514273


And over a couple of days:
View attachment 1514275
Give using the PC Fans on top extracting the heat from the Heat Sink a go.Thats the way I set them up quite some time ago and its been keeping my inverter nice and cool. I am running a 5kw though, but still worth checking out
 

Attachments

  • inverter temp.jpg
    inverter temp.jpg
    29.7 KB · Views: 33
Give using the PC Fans on top extracting the heat from the Heat Sink a go.Thats the way I set them up quite some time ago and its been keeping my inverter nice and cool. I am running a 5kw though, but still worth checking out
I'm not sure this will work. 8kw has an internal heatsink with no ventilation holes on the top
 
Anyone have a Sunsynk/Deye 8kW installed inside the house in a common living area? Is the noise level bearable?
Do the silent fan mod...
Make sure you get silent fans though, like these: https://www.loot.co.za/product/cooler-master-sickleflow-non-led-pc-case-fan-92mm/rhsd-7510-g130
 
Last edited:
Mine has three fans down the side with ventilation holes along the side. I haven't seen any with ventilation along the top
Yes the 8 has fans on the side. The 5 has a massive heat sink accessible from both bottom and top with natural ventilation. It has an internal fan, likely for a processor.
 
Update on my side.

We are up and running and had a solid first day. The installation was stressful to say the least. Still a few niggles to sort out.

We put the system through its paces today, in terms of what a fairly busy day will look like. Geyser, plus washing machine, oven etc. didn't skip a beat!

Trying to learn the system as time goes but thanks to this thread i knew a few things already. I have a few questions though!

In the second attachment, soon after the batteries were full, SOC 99% a big draw came through (the iron i think).
Why did the battery not supply the load with solar like it has been doing. Instead, the grid kicked in and supplied the load with solar. This confused me a bit.
 

Attachments

  • Screenshot_20230427_134612_Sunsynk Connect.jpg
    Screenshot_20230427_134612_Sunsynk Connect.jpg
    71.1 KB · Views: 50
  • Screenshot_20230427_143557_Sunsynk Connect.jpg
    Screenshot_20230427_143557_Sunsynk Connect.jpg
    93.3 KB · Views: 48
Last edited:
Update on my side.

We are up and running and had a solid first day. The installation was stressful to say the least. Still a few niggles to sort out.

We put the system through its paces today, in terms of what a fairly busy day will look like. Geyser, plus washing machine, oven etc. didn't skip a beat!

Trying to learn the system as time goes but thanks to this thread i knew a few things already. I have a few questions though!

In the second attachment, soon after the batteries were full, SOC 99% a big draw came through (the iron i think).
Why did the battery not supply the load with solar like it has been doing. Instead, the grid kicked in and supplied the load with solar. This confused me a bit.
Probably check SYSTEM MODE settings. You'll probably find your system was configured to keep the batteries at 100% at that time you are referring to.
 