But if you want to wire an inverter in, that will have to go before the E/L...
Correct - which means in your case, you would need to upgrade your single pole 'mains' switch, to a double pole. Painful, as it would require Eskom / Council to temporarily switch off your electricity supply to replace the breaker.
Why do you say so? My understanding was that fixed stuff like the stove and geyser did not need to be behind an E/L. They just need to be properly earthed? Your own picture in the "How to wire an inverter into my DB board" had the geyser and stove in front of the E/L? Or is just because of the itchy feeling you get when thinking of getting a shower?
Sorry - I'm confused (10,000 things going on - my mind's wondering a bit)...
6.16.1.3 The power supply to every fixed appliance, except luminaires, shall be supplied through
a) a disconnecting device that disconnects both live conductors in a single-phase supply and all phase conductors in a multiphase supply, or Amdt 3
b) a socket-outlet that is directly accessible at all times that any person is exposed to such appliance while the supply is on. In the case of a remotely installed appliance, the position of the disconnecting device shall be indicated by means of a notice in close proximity to or on the appliance. Amdt 3
6.16.2 Water heaters
NOTE Water heaters include geysers, instantaneous water heaters including units for boiling water, and the like (see also 6.16.1). Amdt 4
6.16.2.1 All water heaters shall be bonded in accordance with 6.13.
6.16.2.2 Dedicated circuits shall be provided for water heaters and there may be more than one water heater on each circuit.
NOTE If a water heater is installed in a bathroom, see table 7.1 regarding earth leakage protection.
6.16.3.3 Stove connection
6.16.3.3.1 A stove designed to be a free-standing appliance rated above 16 A shall be connected through Amdt 4
a) a stove coupler which shall comply with SANS 60309-1/IEC 60309-1 and of dimensions as given in SANS 337 (a maximum of 45 A single-phase and 16 A per phase for three phase), or Amdt 5
NOTE 1 Earth leakage protection is not required for the stove circuit when a stove coupler is used.
Table 7.1 in regards to Geysers basically state that IF your geyser is located IN your Bathroom (Zone 1), E/L is required. Otherwise, you are correct, E/L not required. I do stand corrected here. If you have a stove < 16A, it should connect through a normal plug socket, which should already have E/L protection in any case.
Zone 1 is limited by
a) the vertical plane circumscribing the outer edge or 0,20 m from the inner edge (where the ledge is too wide) of the bathtub, shower basin, or for a shower without a basin, by the vertical plane 0,60 m from the shower rose, and
b) the horizontal plane 2,5 m above the bathtub or shower floor.