TheChamp
Honorary Master
Yes, I worked out the current based on the general specs for these panels, it should be between 8 to just under 10A, all your panels are in series so they are as good as the current of one panel. 10A produces 2300W at 230Vac, which is way low and unlikely to even account for half of your power requirements. Your battery is working overtime during the day, as soon as it's charged it must get back to work so there is hardly time for it to maintain the charge.From the manual the default maximum charging current is set to 60A and the maximum utility charging current is set to 30A. I’m pretty sure these settings haven’t been changed but I’ll check later.
Excuse my ignorance, but I’m assuming you worked out the solar current of 10A from my solar set up, and knowing the other settings, what does this mean regarding the solar proving power to the house during the day? Does this more of less mean it’s not doing much due to the small number of panels? Would you recommend I change some settings somehow?
The settings should be changed because I don't think the default are set to lithium. 60A looks fine for total current but if AC is set for 30A and solar can only produce 10A it looks like you have a shortfall of charging current, I am assuming the 4.8kWh will need between 50 to 60A but check on the battery specs and see what current is recommended, you will then need to up your AC charging current accordingly since AC is basically the primary charging source since there's not much to work with from solar, 30A from AC sounds slightly low.