I think I am going to charge to 100% today and do the cell rebalancing. Otherwise It might've been a miscommunication between the BMS and the inverter so will maybe do a firmware upgrade on both battery and inverter.Yes, it should switch to grid in that situation.
Not that quickly. Something definitely odd there, no way it should drain the battery UNLESS your battery has the old SOC drift I moan about and it wasn't really at 50%. Can you see your battery voltage at the time? When outputting high , the voltage is at a lower state but it also recover a bit to the correct level once that drops.
ie: If I run at about 1KVA and my voltage is 49V and it drops about 0.03V per minute of consumption at 1KVA, then I would expect in five minutes my voltage to be 48.75V but if I have a high output at say 4KVA not only will I suffer the drop in voltage from the actual energy discharged but there is a temporary higher loss. So it runs for 2 mins at the high rating, the voltage reading will actually reflect 48.5V while outputting high or slightly lower but will return to the similar voltage it would be at 1KVA when the draw lessens, minus the energy expected discharge loss of voltage ( 48.75V ).
Voltage was pretty constant throughout.