A single (white) panel'ed DB board, with 1 'mains breaker' and 1 'alternative power' breaker, having say 5 10A breakers and 5 20A breakers, is NOT clear seperation. Even though you have an breaker marked 'alternative power', there is still uncertainty as to which of the 10A and 20A breakers are fed from which supplies (if that makes sense). In other words, I can switch off your 'alternative supply', but I still won't know which of your 10A or 20A breakers are energized or not. This is a good example of a single (split) DB, which does NOT have adequate separation.
Invalid Attachment specified. If you followed a valid link, please notify the administrator
Regarding the separation - If you have all your UPS isolators, E/L and breakers in a clearly marked section of the DB, grouped together, I really can't see why that would be a problem. It is clearly separated.
What is suitable separation will always be up to interpretation I suppose.
That's exactly the point yes. IMHO also the reason why most would recommend (I'm not sure about the -insist- bit) to have it in a separate board... A separate board CANNOT be misinterpreted.
Again, IMHO, you're already spending 40K+ on a decent system (Batteries + Inverter)... 100K+ if going solar. Don't be a cheap skate, spend the R500 odd, and buy a seperate board. You will have to pay for the breakers in any case, whether you have a separate board or not, so the additional few bobs for a separate board, really, should not even be an issue.
A small 8-Way DB (which should be sufficient if you plan carefully), isn't even R300...
I was (and still am) hoping to get away with a split DB. The DB is in the passage between the bedrooms, built into the wall, hence my reason hoping that a second DB could be avoided.
Here's another question: Can you have normal supply and emergency supply in the same conduit?
The Axpert looks very similar (identical?) to the models supplied by MPP Solar in Taiwan (http://www.mppsolar.com)
Can someone with experience in these units confirm :
- Noise levels on a 3kVA or similar Axpert - i.e. fan noise, buzzing. Is there noise when running off mains supply? Or only noise during mains failure? Is the noise tolerable enough to place the unit in the living area e.g. lounge area
- If running low power load i.e. <1000 watts, could this unit be used in a non-fixed manner - e.g. connected unmounted next to a TV cabinet (firmly secured in place).
- If connected as a UPS device (Input to unit from wall plug, output to multiplug) as in 2 above, would one still recommend breakers/EL etc? Is this scenario in point 3 feasible? i.e. not connected to the DB but as a standalone unit with input from wall plug as stated above.
Ok, so last night I changed my wiring so that the 20A single breaker that feeds the Axpert is fed from right after the main 60A dp breaker, so before the earth leakage. Then I bonded the neutral and earth on the output of the Axpert as recommended by savage. Tested it and all is happy. No more floating neutral in battery mode.
So, my DB has 3 sections: main breaker (dp 60A), which feeds geyser, stove and inverter breakers, as well as the EL. The EL section feeds 3 plug circuit breakers. Lastly, the inverter feed comes back in to a 20A dp breaker, which feeds a 10A dedicated plug circuit and a 10A light circuit.
I still have to clean up the DB so that it is partitioned better, having the main & EL section on the top row and the inverter section on the bottom row. Then mark it clearly and add the power present indicator lights.
I don't have an EL on the inverter output, as I have dedicated type red sockets on that circuit but I may add one later for safety's sake.
Getting there slowly...
That's exactly the kind of setup I would like, but I think the 5K will be overkill for my needs. I will most probably look at a 3K, hell even a 1K might work for the little I need to power (thinking loadshedding only at this stage)![]()