- The third option is to put a larger battery on the UPS. What is the largest capacity battery one can safely connect up to a UPS this way?
I am no guru, but there is no limit on the capacity of the battery one can connect to a UPS. Your two main issues here, from what I know (please feel free to correct me):
- Limit in the charging circuit.
The charger in the UPS might only be x Amps and will obviously take longer to charge a 100Ah battery compared to the 7Ah it was designed to charge. With the higher stages of loadshedding you might run into the issue of not having enough time between loadshedding to get the batteries charged up sufficiently. - The heat factor.
The UPS and charger might not have been designed to be in constant charge mode. My UPS is rated to take 4-6 hours to charge the small 7Ah battery inside of it and can thus 'handle' the heat generated by something like that. I upgraded it to 2 x 9Ah and I am thus forcing the UPS to work doubletime. Technically I should be charging the batteries from a charger that was designed to be in a constant charging state and that can handle the heat. That, or I must charge the batteries externally.